That looks like an inverter board - not a soft start. These systems normally use variable speed rotary compressors.
To check compressor.
Remove the compressor wiring connections and meter out the three terminals between each other. They are normally marked something like UVW. So, you would meter u-v, u-w and v-w. The resistance should be the same between each winding. The resistance could be checked against the compressor manufacturers data, but is often quite low at 1-2 ohms. If ok, the windings are good. However, that does not mean the comp may not be seized. However, if that was the case they should have realised that on startup,as it would have made a noise and locked out. They should check the windings to earth as well.
Not so easy to check the inverter board, as it varies the frequency according to load.
Best way is to use an inverter checker like as in the link. Any decent a/c company would have an inverter checker.
http://www.edcpumps.com/en/inverter-phase-check.php
You can't just use any old inverter checker, as these compressors are dc three phase and not ac.
It could also be simpler things like no power getting to the inverter due to a faulty relay / loose or burnt wiring.
They need to check if power is actually getting to the inverter.