11

Re: Gas Combi Boiler

Originally Posted by fender ->
Very odd......

Combi's are used all the time with microbore. The heating will only have a flow of circa 1.5 bar.

Was it an apprentice heating engineer that said that?
Even if the hot water outlet to the taps was in microbore (which would be extremely odd!!!), these pipes and joints are more than capable of taking pressures up to 9 bar at 60%. according to Hep2o's own speccs (http://www.tglynes.co.uk/downloads/t...erformance.pdf).

Maybe the engineer used this fact and ALL of the wet pipework was in 10mm and the supply to the house is over 9bar?
tarantula
Chatterbox
tarantula is offline
UK
Joined: Feb 2016
Posts: 9,359
tarantula is female  tarantula has posted at least 25 times and has been a member for 3 months or more 
 
13-09-2018, 11:21 AM
12

Re: Gas Combi Boiler

Originally Posted by Lindyloo ->
What a blissful summer! My gas bills are incredibly low. Now we're beginning to see a few evenings with lower temperatures. Tonight the temperature inside my home is 20 C and as I walked through the door I heard my gas boiler fire up..............which is the second or third time I've heard that. WHY? I'm not running a bath or kitchen sink - so I can't see a reason for the boiler to fire up............
Any ideas please?

We have a gas combi boiler but are able to turn off the heating switch until it is required, and just have the hot water on.
Dextrous63
Chatterbox
Dextrous63 is offline
Manchester, UK
Joined: Jan 2016
Posts: 7,727
Dextrous63 is male  Dextrous63 has posted at least 25 times and has been a member for 3 months or more 
 
13-09-2018, 12:31 PM
13

Re: Gas Combi Boiler

Just had a google. One suggestion, which seems to make sense is that they go through a hot water pre-heat cycle intermittently.
fender's Avatar
fender
Chatterbox
fender is offline
SE England
Joined: Jan 2016
Posts: 6,286
fender is male  fender has posted at least 25 times and has been a member for 3 months or more 
 
13-09-2018, 06:37 PM
14

Re: Gas Combi Boiler

Originally Posted by Dextrous63 ->
Just had a google. One suggestion, which seems to make sense is that they go through a hot water pre-heat cycle intermittently.
They do. It's to stop legionella being an issue.
The pre heat cycle kills it off.
fender's Avatar
fender
Chatterbox
fender is offline
SE England
Joined: Jan 2016
Posts: 6,286
fender is male  fender has posted at least 25 times and has been a member for 3 months or more 
 
13-09-2018, 06:40 PM
15

Re: Gas Combi Boiler

Originally Posted by Dextrous63 ->
Even if the hot water outlet to the taps was in microbore (which would be extremely odd!!!), these pipes and joints are more than capable of taking pressures up to 9 bar at 60%. according to Hep2o's own speccs (http://www.tglynes.co.uk/downloads/t...erformance.pdf).

Maybe the engineer used this fact and ALL of the wet pipework was in 10mm and the supply to the house is over 9bar?
Hot & cold would still be 15mm / 22mm as appropriate.
Even if the mains inlet is high, you'd just fit an adjustable pressure reducing valve inline. Only the heating should branch off in microbore.
OldGreyFox's Avatar
OldGreyFox
Chatterbox
OldGreyFox is offline
South Yorkshire
Joined: Feb 2015
Posts: 21,202
OldGreyFox is male  OldGreyFox has posted at least 25 times and has been a member for 3 months or more 
 
13-09-2018, 07:41 PM
16

Re: Gas Combi Boiler

Originally Posted by Dextrous63 ->
Just had a google. One suggestion, which seems to make sense is that they go through a hot water pre-heat cycle intermittently.
Only if it's turned on Dextrous. If you are running your boiler on 'Economy' that function is turned off, as Fender pointed out some posts ago.

I still believe it's because the thermostatic controller is hovering close to the activation point.....
galty's Avatar
galty
Chatterbox
galty is offline
rainham essex
Joined: Aug 2009
Posts: 6,080
galty is male  galty has posted at least 25 times and has been a member for 3 months or more 
 
13-09-2018, 07:44 PM
17

Re: Gas Combi Boiler

Originally Posted by Dextrous63 ->
Just had a google. One suggestion, which seems to make sense is that they go through a hot water pre-heat cycle intermittently.
I stated that but maybe very badly in post 5.

It might be the case as some old Combis do is just to keep the Hot water in the Combi hot and fires for a few seconds so you have almost hot water out of your tap
Dextrous63
Chatterbox
Dextrous63 is offline
Manchester, UK
Joined: Jan 2016
Posts: 7,727
Dextrous63 is male  Dextrous63 has posted at least 25 times and has been a member for 3 months or more 
 
14-09-2018, 06:26 AM
18

Re: Gas Combi Boiler

Originally Posted by fender ->
Hot & cold would still be 15mm / 22mm as appropriate.
You'd have thought so, but who knows what might have been installed in realspeed's house I think 10mm is used in caravans and some dodgy cowboy might have thought it's be a good idea to put it in a house!!!!
Originally Posted by galty ->
I stated that but maybe very badly in post 5.
So you did, as indeed did Morty in post 2.
Dextrous63
Chatterbox
Dextrous63 is offline
Manchester, UK
Joined: Jan 2016
Posts: 7,727
Dextrous63 is male  Dextrous63 has posted at least 25 times and has been a member for 3 months or more 
 
14-09-2018, 06:28 AM
19

Re: Gas Combi Boiler

Originally Posted by OldGreyFox ->
Only if it's turned on Dextrous. If you are running your boiler on 'Economy' that function is turned off, as Fender pointed out some posts ago.
Wasn't aware of that, thanks.

Originally Posted by OldGreyFox ->
I still believe it's because the thermostatic controller is hovering close to the activation point.....
Entirely reasonable explanation too
Originally Posted by fender ->
Hot & cold would still be 15mm / 22mm as appropriate.
You'd have thought so, but who knows what might have been installed in realspeed's house I think 10mm is used in caravans and some dodgy cowboy might have thought it's be a good idea to put it in a house!!!!
Originally Posted by galty ->
I stated that but maybe very badly in post 5.
So you did, as indeed did Morty in post 2.

Anyway, the main thing is that it's perfectly normal and nothing to worry about!
gumbud
Chatterbox
gumbud is offline
australia
Joined: Jan 2014
Posts: 12,372
gumbud is male  gumbud has posted at least 25 times and has been a member for 3 months or more 
 
15-09-2018, 09:00 AM
20

Re: Gas Combi Boiler

Phew - glads that sorted - sounds like grand designs re-visited! but well done lads we have enough tradesmen to build a house here! Morticia can you erhm organize tea and sannies please?
 